I am trying to figure out why HG seems very slow in comparison to ActiveHome Pro when receiving a PLC command, performing a very simple check, then sending out a command on PLC. What I am trying to accomplish is using a SmartLabs ToggleLinc switch to send an X10 command on the power line to turn on a different switch. I use AHP and a custom script to trigger on receiving the first switch and then that sends out the command for the second switch. In AHP, I consistently have to wait just under 2 seconds from the time the button is pressed to when the light turns on. When I use HG, I am seeing between 2-4 seconds (varying time) and up to 8 seconds or not at all on the high end.
The code that I'm using to trigger this action is a modified version of the Smart Light code that is built-in to HG. I have removed all PAUSE delays (either commented out or set to zero in code) but cannot get the interface to work faster.
The thing I'm concerned about is that HG may be using a timer to check for incoming events rather than being triggered by events directly. The code in AHP is event driven, which is why it is consistently <2s. If HG is timer based, that would explain why it can be anywhere between 2 and 4 seconds.
I'm attaching my code for reference. This version is not the final version but one I had available to me on a flash drive. I can post the correct version later on if anyone cares to see it. This version does not compile, but it does give all my code prior to fixing a couple things last night.
-
I updated the code to the final (I believe) version of the Advanced Smart Lights code.
I wrote a quick script to see if running the code in the When.ModuleParameterIsChanging block would be quicker. When I timed this with a stop watch, I found that this code results in the entry lights turning on in just under 3 seconds consistently. I switched back to the AHP setup and it turns on/off the light in under 2 seconds.
I really want to use HomeGenie, but I need to find a way to make this work quicker. Any suggestions?
-
I thought perhaps the slow response was based on using C# rather than the Wizard scripting. I built 2 scripts to test if Wizard scripts run faster. The first turns on the entry lights when status of the switch is on. The second is reverse that (turns lights off when switch goes to off). When I send RF commands, the code runs instantly and appears good. However, when I use PLC to toggle the switch, the code runs very slow.
The attached test codes written in Wizard script language run on average of 3.5 seconds to toggle. The test script in the previous post runs at around 2.8 seconds. The full code runs is a bit more interesting. It takes approximately 2.8 seconds to turn off but 3.2 seconds to turn on.
In any case, these are all much longer than the AHP code. Maybe there is a polling rate that can be increased somewhere?
-
The issue is not in the HG automation engine that is very event based, it could be indeed the XTenLib driver.
I believe that XTenLib could be optimized in many ways.
First, probably the "WaitComplete" function could be turned off (just commenting in the contained code):
https://github.com/genielabs/HomeGenie/blob/master/MIG/Support%20Libraries/XTenLib/XTenManager.cs#L510
Also the reader and the writer threads contain some Monitor.Wait/Pulse for synching the communication.
https://github.com/genielabs/HomeGenie/blob/master/MIG/Support%20Libraries/XTenLib/XTenManager.cs#L655
That code probably could be also cut off or at least optimized.
-
I spent the last hour or so looking through the github code to see if I could follow what it was doing And where the delays could be. I hadn't yet reviewed the XTenLib, but I will now. I was slowed by not knowing the best way to review the code other than in the HTML. What program do you recommend to interface with the github code?
-
You can download the whole source zip and open it as suggested in the README.md:
MonoDevelop / Xamarin Studio: HomeGenie/HomeGenie.sln
- or -
Microsoft Visual Studio: HomeGenie_VS10/HomeGenie_VS10.sln
g.
-
I tried to install Xamarin Studio on my laptop and desktop machines running Win7, but it wasn't happy with installing one of the packages. I'll try again with VS to see if it likes that better. I've used VS in the past, so it's probably a better option anyway.
I noticed there's a 5 second sleep in one of the code segments, but I'm not sure if that could be involved here. If so, the minimum trigger time would have to be much more than 2-3 seconds.
-
I'm still reviewing the code to understand how it's used, but there are 2 locations you suggested checking. The first was the WaitComplete function. The sleep is only 0.1 seconds, so I doubt that would cause too much problem (whatever the code is intended to do). The second function is WriterThreadLoop and the sleep is apparently 3 seconds. This function could certainly cause problems depending on what it's intended to do.
private void WriterThreadLoop()
{
while (true)
{
try
{
if (sendQueue.Count > 0)
{
byte[] msg = sendQueue.Dequeue();
//Console.WriteLine(">>>>>OUT " + Utility.ByteArrayToString(msg));
Monitor.Enter(comLock);
if (isWaitingChecksum && msg.Length > 1)
{
Monitor.Wait(comLock, 3000);
isWaitingChecksum = false;
}
SendMessage(msg);
...
It looks like the code is intended to send the commands to the X10 device (CM15 in this case). If there is something in the SendQueue then Monitor is started (connecting to the correct port). If the isWaitingChecksum is true or the msg length is greater than 1, then it will wait for 3 seconds. I'm not sure why that's needed, but it should only take 500ms or less to send an X10 message on PLC, so 3000ms seems pretty long.
I tried to reduce the delay to 500ms and recompile, but the compiler complained about errors. Perhaps it would be possible to reduce this and post a test exe for me to try? I'll try using Visual Studio 2010, but if this is a simple thing to try, let me know...
-
XTenLib.dll with 500 ms max-wait.
g.
-
I tried that driver and it didn't make a difference (still takes 2.8s to turn on/off the light from the time the switch is toggled). I was confused why until I reviewed the Wait method and realized that it worked differently than a sleep statement. I thought it was a mandatory wait time rather than a max wait until the comLock is unlocked.
There must be something else in the code that is causing a delay. I'll have to review the driver again to see what's going on at a high level so I can be more helpful in optimizing this. I only saw the two delay statements, so I'm not sure what else would cause the delay in this driver (unless the delay is from where the driver is called).
-
I'm curious if this difference in response time could have to do with the compiling? I've read that using the optimization option will dramatically increase the speed of the code. This is primarily due to removing debugging overhead, so I assume it is not being used. If you think this could cause some extra overhead in the code, would it be worth tying a compile with the debug disabled or the optimize option enabled?
Also, it looks like there is a common exe for all platforms. Is there a benefit to compiling specific versions for different OS'es? I'm not an expert on this stuff, so I'm just throwing ideas out that I ran across in my research.
I haven't tried using Mochad for this, so perhaps that would be a good benchmark. I know how fast AHP and the SDK work, but it would be valuable to compare that to an implementation that uses C on Linux to see if I'm right in comparing that to a different hardware config.
-
Hi Ben,
optimizations will be done when HG will become a stable product. Mono has a feature called AOT that will compile to native code.
I don't think the problem is that though.
I was thinking that you could try disabling the "X10 - Dimmer Bright 100% when switched on" program and see if X10 controlling gets somehow faster.
Cheers,
g.
-
I'll try that. But, since this is a relay style light, I would hope that it isn't sending dim/bright commands. It won't hurt anything but it won't do anything either.
I only suggested the optimize option since I read that some code could be run instantaneously with it on and could take several seconds without (that was a math function in a loop of some kind for reference).
I'm also going to test on a Win7 laptop to see if this is a Raspi limitation or related to HG current implementation of the code.
-
I installed r350 on my Win7 laptop and tried the simple test code. The time for the switch to toggle and then the light to turn on was the same as before (2-3 seconds).
I tried one other thing for a reference point. I had mochad installed on one of my raspi SD cards already, so I tried running a simple bash script that takes the switch address and controls the light. This code toggled the light in less than 2 seconds up to 3 seconds. It looks like the raspi can be just as fast as AHP.
-
Yes raspberry is pretty good. The odd things is that I am not able to reproduce your issue. X10 works just fine and response is sometime below 1sec. Still I think that, as you said, the XTenLib can be optimized.
With Philips Hue and Z-Wave the response time is kind of real-time.
g.
-
When I send a command from HG to turn on a light, it takes less than a second for the module to respond. This issue is present for me when I send a command from a X10 controller via PLC or RF to the CM15 and then have the CM15 send a command to the light module by PLC. Are you saying that running this configuration you see the light turn on in less than a second?
-
Ok... so it's a different scenario from the one I figured out.
Tell me what kind of test I can do to reproduce? Do I have to send a command with an RF remote and see if CM15 route it through PLC?
Give me some example.
Cheers,
g.
-
Simple test:
- Install test-C#.hgx
- Configure 2 X10 modules ("Entry lights" and "Entry switch"). The switch doesn't need to have a physical module, but the light must be real module of some kind (preferably a relay style light or appliance module or non-ramping dimmable module). The relay is helpful because it gives an audible notification for when the command is executed by the module.
- With the switch and light both off in HG, send an on command with either an RF or PLC controller (any type should work from my testing).
- With a stop watch, time how long it takes from when you press the on button on the controller to when the relay clicks or the light turns on
The HG interface will obviously show a much slower response than the actual light due to the polling of the web page, but the light itself should ideally turn on very quickly. X10 takes fractions of a second to send, but in practice it should respond in under 1 second. Since this is 2 commands, the best case would be something less than 2 seconds. When this is run via AHP's SDK, the response is 1.5-2 seconds. When run with Mochad, the response seems to be just over 2 seconds (2.1-2.2s). HG seems to take 2.8-3.5 seconds.
It would be good to confirm that this is consistent for you and that it's not something else in my setup that could be improved.
-
I just got a very useful response from a senior member at the X10 forums about optimal time for this operation:
You are actually receiving B6 B_ON and sending A6 A_ON. Given that each code is sent twice and each doublet must be followed by 3 silent cycles, B6 B_ON uses 50 cycles of the powerline. A6 A_ON requires the same amount of time but most X10 receivers will react to the first copy of the function code which would be 36 powerline cycles. So, the minimum time will be 1.43 seconds and this is without any time allowed for the CM15A to react to B6 B_ON and send A6 A_ON.
[url]http://digilander.libero.it/cvolpato/elettronica/X-10_Transmission_Theory.htm[/url]
Basically, best case for this operation would be 1.43s. I'm seeing 1.5s with AHP, so something close to that would be great.
I wrote a little script to use Mochad for this test. I think it's useful in case you wanted to see a comparison of speed.
The other question I had was about the implementation of the USB drivers. I know that Mochad uses the libusb-1.0.0 development drivers since there's nothing built into Linux to handle connecting to the CM15. What drivers are you using in HG? Since they are the same for both Windows and Linux, I'm assuming they are built into .NET 4 framework. Is it possible this is what is slowing things down? If so, perhaps it would be possible to use Mochad with the web helper in HG since Mochad will connect to any TCP client?
-
Hi Ben,
hg is also using libusb. I just sent r351 update that is aimed to solve some threading and memory performance issues.
Pheraps it can give a better x10 response too. Didn't test though.
g.
-
I'm still trying to get r351 to work on my raspi. I've tried the install 2 or 3 times now and each time going from a working 345 image, I get a broken 351.
-
With R345 on raspian with cm15pro i can confirm that x10 is as fast as hue lightning, I tend to say that even x10 is already realtime
BUT, I cannot go further than R345 as mentioned in the bugs thread r350-r351, Gene, we need your help I guess. How can we help providing logs etc?
cheers
Jens
-
It depends on what you mean by fast. If you push a button on the HG display (web or Android), the light will responds very quickly. My question is about sending an X10 command over the PLC, having HG see the command, HG sending a new PLC command, and having the light turn on. In this case, I do not expect things to be instantaneous as the PLC transmission is not capable of being that fast.
I just tested r352 and it appears to be around the same speed. I have logging turned on and am redirecting the output to a file in my /home/pi directory. Watching the contents of this file, I see the following:
2014-03-29T11:38:39.1426200-07:00 HomeAutomation.X10 B6 - Status.Level 1
2014-03-29T11:38:39.4001950-07:00 HomeAutomation.X10 A6 - Status.Level 1
I believe this can be interpreted as HG sees the PLC command at 11:38:39.1426200 and then responds with the reply at 11:38:39.4001950. If so, that is a difference of 0.25 seconds that it took HG to respond. If that's the case, then if I take the optimum time for a transmission to occur 2 ways (1.43s) and add this delta, I'd have 1.687 seconds. I'm still seeing close to 3 seconds though before the light actually turns on.
Is there a way to add more output to the X10 module so that it could output when it receives and when it sends commands? I don't know how much this would help, but it seems like it might be good for debugging to at least try.
-
I just realized I could use HG to log a X10 command sequence. I triggered the switch and let AHP turn the light on. This is what HG logged:
2014-03-29T11:55:52.7697510-07:00 HomeAutomation.X10 B6 - Status.Level 0
2014-03-29T11:55:53.6278830-07:00 HomeAutomation.X10 A6 - Status.Level 0
So, HG saw the PLC B6 OFF at the same time as AHP and after AHP responded, HG saw the command. This means, there could be a slightly longer time than the light would need to toggle. Total time for the command was 0.858 seconds plus the time it takes for the first to be sent (~1.43/2 or 0.72s) which would be ~1.573 seconds.
-
Hi Ben,
just replaced the r356 in the testing folder.
https://sourceforge.net/projects/homegenie/files/testing/
I made some more cleanup and optimization in XTenLib.
Whenever you get a chance, please test it.
Thanks!
g.
-
I'm downloading now. Will let you know.
-
I have r356 installed and running. When I look at the log, I can see all the communication with the CM15A, which is great. The only thing that might be nice would be outputting the time so I could be a bit more precise. Looking at what it's displaying now, I'm seeing the following:
"2014-03-30T18:41:55.3470740-07:00 MIG.Gateways.WebServiceGateway 192.168.0.5 api/HomeAutomation.HomeGenie/Logging/Recent.Last/5000/1396230131702 HTTP GET"
[X10] >> IN 5A 02 00 E9
[X10] >> OUT C3
[X10] >> IN 5A 02 01 E3
"2014-03-30T18:41:58.2072520-07:00 HomeAutomation.X10 B6 - Status.Level 0"
"2014-03-30T18:41:58.2179060-07:00 HomeAutomation.X10 A6 - Status.Level 0"
[X10] >> OUT C3
[X10] >> OUT 04 69
[X10] >> IN 55
[X10] >> OUT 06 63
[X10] >> IN 55
"2014-03-30T18:42:00.3185510-07:00 MIG.Gateways.WebServiceGateway 192.168.0.5 api/HomeAutomation.HomeGenie/Logging/Recent.Last/5000/1396230136697 HTTP GET"
I don't have the exact time for the X10 events, but using the line right after/before yields the following.
Command Time Delta
CM15A sees start of A6 ON sequence 18:41:55.3470740 00:00:00.000
HG recognizes A6 ON sequence 18:41:58.2072520 00:00:02.860
HG starts to send B6 ON sequence 18:41:58.2179060 00:00:02.871
HG finished sending B6 ON sequence 18:42:00.3185510 00:00:04.972
I don't believe the 4.9 seconds at all. My stop watch indicates closer to 2.5-3 seconds or so.
-
So this is what I've found. When I use HG to monitor AHP, this is the incoming activity:
A6 ON
[X10] >> IN 5A 02 00 69
[X10] >> OUT C3
[X10] >> IN 5A 02 01 62
[X10] >> OUT C3
A6 OFF
[X10] >> IN 5A 02 00 69
[X10] >> OUT C3
[X10] >> IN 5A 02 01 63
[X10] >> OUT C3
B6 ON
[X10] >> IN 5A 02 00 E9
[X10] >> OUT C3
[X10] >> IN 5A 02 01 E2
[X10] >> OUT C3
B6 OFF
[X10] >> IN 5A 02 00 E9
[X10] >> OUT C3
[X10] >> IN 5A 02 01 E3
[X10] >> OUT C3
When using HG as the controller:
A6 ON
[X10] >> OUT 04 69
[X10] >> IN 55
[X10] >> OUT 06 62
[X10] >> IN 55
A6 OFF
[X10] >> OUT 04 69
[X10] >> IN 55
[X10] >> OUT 06 63
[X10] >> IN 55
B6 ON
[X10] >> IN 5A 02 00 E9
[X10] >> OUT C3
[X10] >> IN 5A 02 01 E2
[X10] >> OUT C3
B6 OFF
[X10] >> IN 5A 02 00 E9
[X10] >> OUT C3
[X10] >> IN 5A 02 01 E3
[X10] >> OUT C3
As expected, the B6 ON/OFF are the same since those are sent by the wall switch. Also as expected, the A6 ON/OFF are different. In the first case, AHP is sending the A6 ON/OFF and in the second HG is acting as the controller. The only thing I'm wondering is if there's a reason that HG is sending half as many octlets as AHP. I'm wondering if HG is taking 2 cycles to send a single command. If so, then it would definitely take much longer to control the light. In fact, if it takes 1.43 seconds minimum to send 2 commands, then this would effectively be requiring 3 commands or a total of 2.145 seconds plus computing overhead. I'm seeing something on the order of 2.5-3 seconds, so this seems like a plausible explanation.
-
I modified the XTenLib.dll to output the time and ran a few tests. The tests were:
- HG sends B6 ON command, AHP receives it and turns A6 ON, HG sees A6 ON
- HG sends B6 OFF command, AHP receives it and turns A6 OFF, HG sees A6 OFF
- AHP sends B6 ON, HG receives B6 ON and turns B6 ON
- AHP sends B6 OFF, HG receives B6 OFF and turns B6 OFF
I took the commands and created a delta time for these steps. This is not an ideal way to test since I'm still using HG to watch for commands. The best way would be to have a 3rd controller monitor for times, but I don't have that available. As such, the AHP response time should be exactly correct. But, the HG command will not include the time for AHP to send the command nor the time for the response to go over the power lines. I believe this may be critical, but I don't currently have a way to deal with that.
That being said, here's what I found:
command sent from HG web interface
2014-04-05T08:47:20.2184060-07:00 HomeAutomation.X10 B6 - Status.Level 1 08:47:20.2184060
2014-04-05T08:47:20.2457730-07:00 >>>>>OUT 04 E9 08:47:20.2457730
2014-04-05T08:47:20.6611630-07:00 <<<<< IN 55 08:47:20.6611630
2014-04-05T08:47:20.7517040-07:00 >>>>>OUT 06 E2 08:47:20.7517040
2014-04-05T08:47:21.1739230-07:00 <<<<< IN 55 08:47:21.1739230
2014-04-05T08:47:21.5902020-07:00 <<<<< IN 5A 02 00 69 08:47:21.5902020
2014-04-05T08:47:21.6578180-07:00 >>>>>OUT C3 08:47:21.6578180
2014-04-05T08:47:22.0144670-07:00 <<<<< IN 5A 02 01 62 08:47:22.0144670
2014-04-05T08:47:22.0188050-07:00 HomeAutomation.X10 A6 - Status.Level 1 08:47:22.0188050
2014-04-05T08:47:22.1635670-07:00 >>>>>OUT C3 08:47:22.1635670
Command Time Delta
HG command sent (B6 ON) 08:47:20.2184060 00:00:00.000
X10 B6 ON 08:47:20.7517040 00:00:00.534
X10 A6 ON (sent from AHP) 08:47:22.0144670 00:00:01.796
HG understands A6 ON 08:47:22.0188050 00:00:01.801
command sent from HG web interface
2014-04-05T08:55:58.8141920-07:00 HomeAutomation.X10 B6 - Status.Level 0 08:55:58.8141920
2014-04-05T08:55:58.8875600-07:00 >>>>>OUT 04 E9 08:55:58.8875600
2014-04-05T08:55:59.3044940-07:00 <<<<< IN 55 08:55:59.3044940
2014-04-05T08:55:59.3909610-07:00 >>>>>OUT 06 E3 08:55:59.3909610
2014-04-05T08:55:59.6393730-07:00 MIG.Gateways.WebServiceGateway 192.168.0.5 api/HomeAutomation.HomeGenie/Logg$ 08:55:59.6393730
2014-04-05T08:55:59.8165680-07:00 <<<<< IN 55 08:55:59.8165680
2014-04-05T08:56:00.2335510-07:00 <<<<< IN 5A 02 00 69 08:56:00.2335510
2014-04-05T08:56:00.2949440-07:00 >>>>>OUT C3 08:56:00.2949440
2014-04-05T08:56:00.6566460-07:00 <<<<< IN 5A 02 01 63 08:56:00.6566460
2014-04-05T08:56:00.6585640-07:00 HomeAutomation.X10 A6 - Status.Level 0 08:56:00.6585640
2014-04-05T08:56:00.7983860-07:00 >>>>>OUT C3 08:56:00.7983860
Command Time Delta
HG command sent (B6 OFF) 08:55:58.8141920 00:00:00.000
X10 B6 OFF 08:55:59.3909610 00:00:00.577
X10 A6 OFF (sent from AHP) 08:56:00.6566460 00:00:01.843
HG understands A6 OFF 08:56:00.6585640 00:00:01.845
command sent from AHP
2014-04-05T09:00:29.0631090-07:00 <<<<< IN 5A 02 00 E9 09:00:29.0631090
2014-04-05T09:00:29.1476360-07:00 >>>>>OUT C3 09:00:29.1476360
2014-04-05T09:00:29.4871290-07:00 <<<<< IN 5A 02 01 E2 09:00:29.4871290
2014-04-05T09:00:29.4915170-07:00 HomeAutomation.X10 B6 - Status.Level 1 09:00:29.4915170
2014-04-05T09:00:29.5319770-07:00 HomeAutomation.X10 A6 - Status.Level 1 09:00:29.5319770
2014-04-05T09:00:29.6531090-07:00 >>>>>OUT C3 09:00:29.6531090
2014-04-05T09:00:30.1587340-07:00 >>>>>OUT 04 69 09:00:30.1587340
2014-04-05T09:00:30.5786750-07:00 <<<<< IN 55 09:00:30.5786750
2014-04-05T09:00:30.6643090-07:00 >>>>>OUT 06 62 09:00:30.6643090
2014-04-05T09:00:31.0823130-07:00 <<<<< IN 55 09:00:31.0823130
Command Time Delta
X10 B6 ON (sent from AHP) 09:00:29.0631090 00:00:00.000
HG understands B6 ON 09:00:29.4915170 00:00:00.429
HG command sent (A6 ON) 09:00:29.5319770 00:00:00.469
X10 A6 ON 09:00:30.6643090 00:00:01.601
command sent from AHP
2014-04-05T09:06:18.9933690-07:00 <<<<< IN 5A 02 00 E9 09:06:18.9933690
2014-04-05T09:06:19.0666360-07:00 >>>>>OUT C3 09:06:19.0666360
2014-04-05T09:06:19.4165440-07:00 <<<<< IN 5A 02 01 E3 09:06:19.4165440
2014-04-05T09:06:19.4207080-07:00 HomeAutomation.X10 B6 - Status.Level 0 09:06:19.4207080
2014-04-05T09:06:19.4400480-07:00 HomeAutomation.X10 A6 - Status.Level 0 09:06:19.4400480
2014-04-05T09:06:19.5729060-07:00 >>>>>OUT C3 09:06:19.5729060
2014-04-05T09:06:20.0788370-07:00 >>>>>OUT 04 69 09:06:20.0788370
2014-04-05T09:06:20.5010090-07:00 <<<<< IN 55 09:06:20.5010090
2014-04-05T09:06:20.5086860-07:00 MIG.Gateways.WebServiceGateway 192.168.0.5 api/HomeAutomation.HomeGenie/Logging/RealTime.EventStream/ HTTP GET 09:06:20.5086860
2014-04-05T09:06:20.5843740-07:00 >>>>>OUT 06 63 09:06:20.5843740
2014-04-05T09:06:21.0047190-07:00 <<<<< IN 55
Command Time Delta
X10 B6 ON (sent from AHP) 09:06:18.9933690 00:00:00.000
HG understands B6 ON 09:06:19.4207080 00:00:00.428
HG command sent (A6 ON) 09:06:19.4400480 00:00:00.447
X10 A6 ON 09:06:20.5843740 00:00:01.591
So:
- 00:00:01.801
- 00:00:01.845
- 00:00:01.601
- 00:00:01.591
The total time it takes AHP to toggle a light when HG sends the command is 1.8-1.85 seconds. The time it takes for HG to toggle a light is 1.6 seconds plus transmission time (probably half of the 1.43 seconds, or 0.715 seconds) or 2.3 seconds. I'm still seeing much longer (closer to 3 seconds).
-
I wonder if all these >>>>>OUT C3 are really needed. Perhaps this is the problem. HG is sending unneeded "Poll Reply" (0xC3).
Maybe these should only be sent in presence of a single byte input message 0x5A (poll request).
Currently HG seem to send poll reply everytime the input message starts with 0x5A.
Can you see how do AHP behaves? Do AHP log messages sent to the interface?
Anyway I will give it a try making HG send poll reply only when a single byte is received and see if everything continues to work.
Cheers,
g.
-
Seem to work.
I replaced the lines:
(https://github.com/genielabs/HomeGenie/blob/master/MIG/Support%20Libraries/XTenLib/XTenManager.cs#L395)
else if ((readData[0] == (int)X10CommandType.PLC_Poll)) // && readdata.Length > 2)
{
statusRequestOk = true;
sendQueue.Enqueue(new byte[] { 0xC3 }); // reply to poll
with:
else if ((readData[0] == (int)X10CommandType.PLC_Poll) && readData.Length == 1)
{
statusRequestOk = true;
sendQueue.Enqueue(new byte[] { 0xC3 }); // reply to poll
}
else if ((readData[0] == (int)X10CommandType.PLC_Poll))
{
g.
-
I replaced the code and recompiled. It does appear to run quicker. Interestingly, one time, the code seemed to work way too fast (~0.75 seconds), but that seems to be an outlier. The new times indicate the average time is now between 1.3 and 1.4 seconds plus overhead after the send. I used the stopwatch and found the change occurs in just over 2 seconds (2.2 or so seconds). This is a huge improvement!
The one thing that stands out about the code that's being printed to the log is that HG seems to send 4 characters (2 sets of 2 digit hex) whereas AHP seems to be sending 8 characters (4 sets of 2 digit hex).
HG will send:
04 E9
06 E2
and
04 E9
06 E3
AHP will send:
5A 02 00 E9
5A 02 01 E2
and
5A 02 00 E9
5A 02 01 E3
-
Hi Ben,
HG and AHP transmit the same number of bytes. What are you seeing is just extra bytes from the CM interface that tells the software what kind of data is being received (RF, PLC, MACRO etc...) and the length of the received data (02).
Cheers,
g.
-
That makes sense. I still think it's possible to squeeze a little more speed out since mocha was able to perform the task in under 2 seconds (though it was not consistent as I recall).
-
I just reviewed my findings during earlier testing with Mochad posted in this thread since I couldn't locate my local documentation. It looks like Mochad runs the 2 command test in 2.1-2.2 seconds. It looks to me as though HG is running basically the same speed at around 2.2 seconds. It would be great if another half second could be squeezed out of this, but I'm not sure if that is possible. Mochad seems to be as lean as things can get and if HG is matching that, then it's unlikely we could do any better without a X10 software programmer telling us a "perfect" solution.
-
I was just thinking about the maximum speed of either Mochad or HG running on Raspi and wondering if this has to do with either the Raspi or the USB drivers being used. If it's drivers slowing things down, that would require either something integrated into the Linux kernel itself probably. But, if it's Raspi, could overclocking help? I've seen people running XBMC et. al. running up to 1GHz pretty regularly with only additional cooling fins. Would a higher clock rate increase the USB performance though? I really have no experience with how the clock speed affects bus transfer rate so this is a serious question.
Also, I'll try running this test on a Windows 7 machine to see if the speed is the same. If so, then the Raspi itself shouldn't be the limitation.